Hi Faryal,
I'm confused as I don't see the problem. When you have a meter-based PM and you have selected the Do not estimate and Generate WO when reached, it will only generate the WO only after the Units to Go has reached or exceeded the 0 value. In other words, the meter reading needs to exceed 57,582.
With you saying the Units to Go is still 853, then you still need to consume 853 more hours (?).
There is no date to be considered. It relies on using up all the hours.
Hope that helps.
------------------------------
Regards,
Craig Kokay
Principle Consultant
Cosol
https://cosol.global/Ph: +61-411-682-040
email:
craig.kokay@cosol.global------------------------------
Original Message:
Sent: Thu September 07, 2023 02:40 AM
From: Faryal Amjad
Subject: Maximo PM (Meter base frequency Workorder is not generated automatically )
Hi ,
I have query regarding the PM meter base workroders.
Frequency : 2,000.00 and Units to Go reaches to 853.00 but auto workorder is not generated after checked the logs from server.
Below warnings appear : Generate work order from PMs on site WW finished 9/6/23 4:55 PM.
<br>BMXAA3191E - PM RTG4MM5H-21-N is not due yet, or it does not fall within the active season.
<br>BMXAA9342W - The next due date is not specified for floating PM RTG4MM5H-21-N in site WW.
To generate the PM, in the PM application, specify a next due date.
PM with checks for generating work orders.
Attached is the screen shot for PM with details.
Pls help if anyone
Regards,
Faryal
------------------------------